0 LOCATION = 'SW Circuit 3' [DonorCircuit] Connected kVA: 4950 Load Utilisation: 0 # of LOAD POINTS: 3 [0 customers, 0 sensitive] # of NOPs: 1 # of ISOL SWITCHES: 5 # of components: 91 => COST: 0.000 LOCATION = 'SW Circuit 8' [DonorCircuit] Connected kVA: 5170 Load Utilisation: 0 # of LOAD POINTS: 1 [2 customers, 0 sensitive] # of NOPs: 0 # of ISOL SWITCHES: 2 # of components: 31 => COST: 2.000 LOCATION = 'SW Circuit 5' [DonorCircuit] Connected kVA: 4290 Load Utilisation: 0 # of LOAD POINTS: 6 [0 customers, 0 sensitive] # of NOPs: 4 # of ISOL SWITCHES: 12 # of components: 209 => COST: 0.000 LOCATION = 'SW Circuit 1' [InitialOutage] Connected kVA: 1100 Load Utilisation: 0 # of LOAD POINTS: 9 [61 customers, 1 sensitive] # of NOPs: 4 # of ISOL SWITCHES: 20 # of components: 339 => COST: 62.000 LOCATION = 'T4' [Outage] Connected kVA: 110 Load Utilisation: 0 # of LOAD POINTS: 2 [8 customers, 0 sensitive] # of NOPs: 1 # of ISOL SWITCHES: 3 # of components: 63 => COST: 8.000 LOCATION = 'T99' [Outage] Connected kVA: 440 Load Utilisation: 0 # of LOAD POINTS: 5 [39 customers, 0 sensitive] # of NOPs: 3 # of ISOL SWITCHES: 9 # of components: 181 => COST: 39.000 NOP: 'NOP 1' [k005513c0COMP] Proximity: 1 Transformer CB: 'k00550f97COMP', rating=1000.0, extra= 10.0, amps=[ 610.0 -> 620.0], spare=[ 390.0 -> 380.0], utilisation=[61.00% -> 62.00%] Feeder CB: 'k00550f67COMP', rating= 500.0, extra= 10.0, amps=[ 410.0 -> 420.0], spare=[ 90.0 -> 80.0], utilisation=[82.00% -> 84.00%] Limiting: 'k00550f67COMP', rating= 500.0, extra= 10.0, amps=[ 410.0 -> 420.0], spare=[ 90.0 -> 80.0], utilisation=[82.00% -> 84.00%] NOP: 'NOP 2' [k005513c9COMP] Proximity: 1 Transformer CB: 'k00550fa1COMP', rating=1000.0, extra= 40.0, amps=[ 390.0 -> 430.0], spare=[ 610.0 -> 570.0], utilisation=[39.00% -> 43.00%] Feeder CB: 'k00550f71COMP', rating= 511.0, extra= 40.0, amps=[ 390.0 -> 430.0], spare=[ 121.0 -> 81.0], utilisation=[76.32% -> 84.15%] Limiting: 'k00551517COMP', rating= 30.0, extra= 40.0, amps=[ 0.0 -> 40.0], spare=[ 30.0 -> -10.0], utilisation=[ 0.00% -> 133.33%] NOP: 'NOP 99' [k005513d0COMP] Proximity: 1 Transformer CB: 'k00550fa1COMP', rating=1000.0, extra= 40.0, amps=[ 390.0 -> 430.0], spare=[ 610.0 -> 570.0], utilisation=[39.00% -> 43.00%] Feeder CB: 'k00550f71COMP', rating= 511.0, extra= 40.0, amps=[ 390.0 -> 430.0], spare=[ 121.0 -> 81.0], utilisation=[76.32% -> 84.15%] Limiting: 'k00551527COMP', rating= 30.0, extra= 40.0, amps=[ 0.0 -> 40.0], spare=[ 30.0 -> -10.0], utilisation=[ 0.00% -> 133.33%] NOP: 'NOP 77' [k005514bcCOMP] Proximity: 1 Transformer CB: 'k00550fc7COMP', rating=1000.0, extra= 40.0, amps=[ 470.0 -> 510.0], spare=[ 530.0 -> 490.0], utilisation=[47.00% -> 51.00%] Feeder CB: 'k00550fccCOMP', rating= 500.0, extra= 40.0, amps=[ 470.0 -> 510.0], spare=[ 30.0 -> -10.0], utilisation=[94.00% -> 102.00%] Limiting: 'k00550fccCOMP', rating= 500.0, extra= 40.0, amps=[ 470.0 -> 510.0], spare=[ 30.0 -> -10.0], utilisation=[94.00% -> 102.00%] NOP: 'NOP 2' [k005513c9COMP] TRANSFER: 'T5' [k00551082COMP] (order=1) Proximity: 1 Transformer CB: 'k00550fa1COMP', rating=1000.0, extra= 15.0, amps=[ 390.0 -> 405.0], spare=[ 610.0 -> 595.0], utilisation=[39.00% -> 40.50%] Feeder CB: 'k00550f71COMP', rating= 511.0, extra= 15.0, amps=[ 390.0 -> 405.0], spare=[ 121.0 -> 106.0], utilisation=[76.32% -> 79.26%] Limiting: 'k00551517COMP', rating= 30.0, extra= 15.0, amps=[ 0.0 -> 15.0], spare=[ 30.0 -> 15.0], utilisation=[ 0.00% -> 50.00%] NOP: 'NOP 77' [k005514bcCOMP] Proximity: 1 Transformer CB: 'k00550fc7COMP', rating=1000.0, extra= 25.0, amps=[ 470.0 -> 495.0], spare=[ 530.0 -> 505.0], utilisation=[47.00% -> 49.50%] Feeder CB: 'k00550fccCOMP', rating= 500.0, extra= 25.0, amps=[ 470.0 -> 495.0], spare=[ 30.0 -> 5.0], utilisation=[94.00% -> 99.00%] Limiting: 'k00550fccCOMP', rating= 500.0, extra= 25.0, amps=[ 470.0 -> 495.0], spare=[ 30.0 -> 5.0], utilisation=[94.00% -> 99.00%] NOP: 'NOP 99' [k005513d0COMP] TRANSFER: 'T5' [k00551082COMP] (order=1) Proximity: 1 Transformer CB: 'k00550fa1COMP', rating=1000.0, extra= 15.0, amps=[ 390.0 -> 405.0], spare=[ 610.0 -> 595.0], utilisation=[39.00% -> 40.50%] Feeder CB: 'k00550f71COMP', rating= 511.0, extra= 15.0, amps=[ 390.0 -> 405.0], spare=[ 121.0 -> 106.0], utilisation=[76.32% -> 79.26%] Limiting: 'k00551527COMP', rating= 30.0, extra= 15.0, amps=[ 0.0 -> 15.0], spare=[ 30.0 -> 15.0], utilisation=[ 0.00% -> 50.00%] NOP: 'NOP 77' [k005514bcCOMP] Proximity: 1 Transformer CB: 'k00550fc7COMP', rating=1000.0, extra= 25.0, amps=[ 470.0 -> 495.0], spare=[ 530.0 -> 505.0], utilisation=[47.00% -> 49.50%] Feeder CB: 'k00550fccCOMP', rating= 500.0, extra= 25.0, amps=[ 470.0 -> 495.0], spare=[ 30.0 -> 5.0], utilisation=[94.00% -> 99.00%] Limiting: 'k00550fccCOMP', rating= 500.0, extra= 25.0, amps=[ 470.0 -> 495.0], spare=[ 30.0 -> 5.0], utilisation=[94.00% -> 99.00%] NOP: 'NOP 1' [k005513c0COMP] Proximity: 1 Transformer CB: 'k00550f97COMP', rating=1000.0, extra= 10.0, amps=[ 610.0 -> 620.0], spare=[ 390.0 -> 380.0], utilisation=[61.00% -> 62.00%] Feeder CB: 'k00550f67COMP', rating= 500.0, extra= 10.0, amps=[ 410.0 -> 420.0], spare=[ 90.0 -> 80.0], utilisation=[82.00% -> 84.00%] Limiting: 'k00550f67COMP', rating= 500.0, extra= 10.0, amps=[ 410.0 -> 420.0], spare=[ 90.0 -> 80.0], utilisation=[82.00% -> 84.00%] NOP: 'NOP 2' [k005513c9COMP] Proximity: 1 Transformer CB: 'k00550fa1COMP', rating=1000.0, extra= 40.0, amps=[ 390.0 -> 430.0], spare=[ 610.0 -> 570.0], utilisation=[39.00% -> 43.00%] Feeder CB: 'k00550f71COMP', rating= 511.0, extra= 40.0, amps=[ 390.0 -> 430.0], spare=[ 121.0 -> 81.0], utilisation=[76.32% -> 84.15%] Limiting: 'k00551517COMP', rating= 30.0, extra= 40.0, amps=[ 0.0 -> 40.0], spare=[ 30.0 -> -10.0], utilisation=[ 0.00% -> 133.33%] NOP: 'NOP 99' [k005513d0COMP] Proximity: 1 Transformer CB: 'k00550fa1COMP', rating=1000.0, extra= 40.0, amps=[ 390.0 -> 430.0], spare=[ 610.0 -> 570.0], utilisation=[39.00% -> 43.00%] Feeder CB: 'k00550f71COMP', rating= 511.0, extra= 40.0, amps=[ 390.0 -> 430.0], spare=[ 121.0 -> 81.0], utilisation=[76.32% -> 84.15%] Limiting: 'k00551527COMP', rating= 30.0, extra= 40.0, amps=[ 0.0 -> 40.0], spare=[ 30.0 -> -10.0], utilisation=[ 0.00% -> 133.33%] NOP: 'NOP 77' [k005514bcCOMP] Proximity: 1 Transformer CB: 'k00550fc7COMP', rating=1000.0, extra= 40.0, amps=[ 470.0 -> 510.0], spare=[ 530.0 -> 490.0], utilisation=[47.00% -> 51.00%] Feeder CB: 'k00550fccCOMP', rating= 500.0, extra= 40.0, amps=[ 470.0 -> 510.0], spare=[ 30.0 -> -10.0], utilisation=[94.00% -> 102.00%] Limiting: 'k00550fccCOMP', rating= 500.0, extra= 40.0, amps=[ 470.0 -> 510.0], spare=[ 30.0 -> -10.0], utilisation=[94.00% -> 102.00%]